david
Senior Member
- Location
- Pennsylvania
225.1 scope never mentions what the source is, so it doesn't matter if that second source is from service or on site production, a feeder is a feeder, a branch circuit is a branch circuit. There is as mentioned in 225 and 230 the "unless permitted in...." which allows additional supplies in both sections for emergency systems, fire pumps, different characteristics, etc. .
you are correct the source in the scope of 225.1 is not identified
225.30 states building supplied from the load side of the service and we know the intent is to limit building supplies.
if we strictly go by the literal reading when the premise source is a on site production such as a generator or solar or anything other than a utility than the number of branch circuit supplies and feeder supplies to additional buildings is no longer a concern
literally 225.30 only addresses feeders and branch circuit supplies to buildings when the premise has a utility service and the branch circuits and feeders are on the load side of the service
What the NEC is intending here is hard to pin point, if additional supplies to buildings need to be closely scrutinized than this section needs to be more clear, if additional supplies to buildings raises a caution or concern than it should be true no matter the source
Last edited: