F frank Member Location Illinois Mar 4, 2003 #1 if i install one 200 amp single phase service and one 3 phase corner gronded delta 100 amp 3 feet apart can i use the same ground rod.
if i install one 200 amp single phase service and one 3 phase corner gronded delta 100 amp 3 feet apart can i use the same ground rod.
charlie Senior Member Location Indianapolis Mar 5, 2003 #3 Re: two services one ground rod ? Not only does 250.58 say you can use the same electrode, it requires you to use the same electrode.
Re: two services one ground rod ? Not only does 250.58 say you can use the same electrode, it requires you to use the same electrode.
V vanwalker Senior Member Location lancaster Mar 5, 2003 #4 Re: two services one ground rod ? YES 250.56 also GEO