D domnic Senior Member Occupation Electrical Contractor May 18, 2018 #1 Can I run two sets of service of under ground in the same trench one three phase and one single phase from poco pole to two meter bases?
Can I run two sets of service of under ground in the same trench one three phase and one single phase from poco pole to two meter bases?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) May 18, 2018 #2 As far as the NEC is concerned, you can.
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Occupation Electrician May 18, 2018 #3 augie47 said: As far as the NEC is concerned, you can. Click to expand... I concur, and would add that it may be worth mentioning that the disconnect(s) for each service do not have to be grouped in one location.
augie47 said: As far as the NEC is concerned, you can. Click to expand... I concur, and would add that it may be worth mentioning that the disconnect(s) for each service do not have to be grouped in one location.