Question? Can you install UG conduit within 5' of a pool that is not related to the pool install?
First sentence says NO, second says Yes.....
Who makes the call on which sentance to use and why?
First sentence says NO, second says Yes.....
680.10 Underground Wiring Location.
Underground wiring shall not be permitted under the pool or within the area extending 1.5 m (5 ft) horizontally from the inside wall of the pool unless this wiring is necessary to supply pool equipment permitted by this article. Where space limitations prevent wiring from being routed a distance 1.5 m (5 ft) or more from the pool, such wiring shall be permitted where installed in rigid metal conduit, intermediate metal conduit, or a nonmetallic raceway system. All metal conduit shall be corrosion resistant and suitable for the location. The minimum burial depth shall be as given in Table 680.10.
Who makes the call on which sentance to use and why?