Two sources of power, same voltage

Status
Not open for further replies.

Mavric

New member
Location
Grant, Nebraska
According to NEC Section 230, you can only have one service at a specific voltage into a building or structure. Is there anything similar for a service that is not a building or structure, e.g. an outdoor motor?
 
According to NEC Section 230, you can only have one service at a specific voltage into a building or structure. Is there anything similar for a service that is not a building or structure, e.g. an outdoor motor?

I would call it a structure

The NEC definition of structure is 'that which is built or constructed'
 
I would call it a structure

The NEC definition of structure is 'that which is built or constructed'
That will be cleared up in the 2017. The words "other than equipment" have been added to the end of the existing definition for the 2017 edition.
 
Well in this case it's is moot because it is equipment requiring power.

OP did not state the reason for two sources, which will be critical to an AHJ's decision to permit a second service.
 