OK.another consideration
fla to both coils ~ 327
i from shorted coil 158
this means i from other coil ~ 327 - 158 = 169
balance 164 +/- 5-6 A or +/- 3.5%
v drop/coil to wye center
lo : 330 x 0.05 x 110/1000 = 1.8 (based on supply to wye center, shorted at motor)
so ~ 275 across lo coil
hi: and from before 5.2 across hi since it has the #2 in the path to the wye center
i delta (277-1.8)/(277-5.2) = 1.5% max assuming coil z is identical
How does explain the 45A difference in current between a good motor and the bad motor?