I apologize for the delay. I have been out of the office and had no internet access during my sabbatical. I thought I would post my findings as of yet for the previous thread that everyone was so kind to post ideas, advice, and experience for.
As yet I finally received motor reports from our motor repair shop for our problem motor and another that was repaired some time back. They ran both motors in High at roughly 452VAC. Our problem motor in high drew current at roughly 160A. Our non problem motor drew current at roughly 103A. At this point we're looking to pull our problem motor and send for re-winding.
The lesson for me is, I should have had reports in front of me instead of relying on verbatim from the motor shop.
As yet I finally received motor reports from our motor repair shop for our problem motor and another that was repaired some time back. They ran both motors in High at roughly 452VAC. Our problem motor in high drew current at roughly 160A. Our non problem motor drew current at roughly 103A. At this point we're looking to pull our problem motor and send for re-winding.