Easy to say from your keyboard
Maybe easy to do with a 2 or even 25 HP motor when compared to a 250 Hp motor.
With that big of a motor, I might be more likely to pull it and have them run it on some kind of dynamometer and if it passes that, time to look into the driven load. But has been mentioned time and time again that the problem exists even without the load coupled to the motor, so unless there is significant voltage change measured as well as high current there about has to be an issue in the motor, but maybe one possibly tries an alternate feed (even if temporarily installed) to this motor if there is any suspicion in the supply circuit.