JohnDS
Senior Member
- Location
- Suffolk, Long Island
- Occupation
- Electrician
Ok,
Customer has a 100amp sub panel installed in the attic of bathroom. This subpanel is powering the bath lighting and receptacle outlets and two steamists. Each steamist has #6 romex run to it and each on a 60amp breaker. One of the steamists is tripping its breaker and it is clear why according to specs. Whats weird is that customer says both been working fine for 3 or 4 months. Actually I am surprised the sub panel main breaker is not tripping. Here are the specs.
My questions are:
1) Why does the manufacturer have such an upsized breaker on the Tsg-15? It says 63amps and 80amp breaker?
2) I am pretty sure the tsg-15's #6 is not correct for an 80amp breaker, so would #4 be ok?
Sent from my SAMSUNG-SM-G730A using Tapatalk
Customer has a 100amp sub panel installed in the attic of bathroom. This subpanel is powering the bath lighting and receptacle outlets and two steamists. Each steamist has #6 romex run to it and each on a 60amp breaker. One of the steamists is tripping its breaker and it is clear why according to specs. Whats weird is that customer says both been working fine for 3 or 4 months. Actually I am surprised the sub panel main breaker is not tripping. Here are the specs.
My questions are:
1) Why does the manufacturer have such an upsized breaker on the Tsg-15? It says 63amps and 80amp breaker?
2) I am pretty sure the tsg-15's #6 is not correct for an 80amp breaker, so would #4 be ok?
Sent from my SAMSUNG-SM-G730A using Tapatalk