I have a question about these two string combining tees.
My concern is having to derate, for temp, conduit greater than 24", etc.
Also even though we are using snake tray, should I have to derate for elevated temps on the
roof?
260 watt module
Isc 9.08
9.08 x 1.25 = 11.35
11.35 x 2 strings in parallel = 22.7 Amps
#10 USE-2 in "Free Air" = 50 Amps 75 deg column
With 14 strings in the system, paralleled (7 strings). I'm looking at about 14 wires in the snake
tray.
Where do I need to derate?
310.15 (b)(3)
50% due to the wires in the snake tray being bundled together?
50 x .50 = 25 amps
The (#10 use-2) still looks good.
Should there be any temp derates for the rooftop?
Is there anything that I'm missing?
My concern is having to derate, for temp, conduit greater than 24", etc.
Also even though we are using snake tray, should I have to derate for elevated temps on the
roof?
260 watt module
Isc 9.08
9.08 x 1.25 = 11.35
11.35 x 2 strings in parallel = 22.7 Amps
#10 USE-2 in "Free Air" = 50 Amps 75 deg column
With 14 strings in the system, paralleled (7 strings). I'm looking at about 14 wires in the snake
tray.
Where do I need to derate?
310.15 (b)(3)
50% due to the wires in the snake tray being bundled together?
50 x .50 = 25 amps
The (#10 use-2) still looks good.
Should there be any temp derates for the rooftop?
Is there anything that I'm missing?