Hello,
We have a 2500A, 3-pole, 4-w, 480v/277v transfer switch (MTS) with main bonding jumper on the normal. The ATS has a 2500AT/2500AF breaker with GFP on the main and swtich only on the emergency source. It feeds an MCC inside a building that has a 2500A main with GFP.
We would like to bring in a second utility to the emergency source (not generator but utility). I use 250.24 for the main service and was thinking to apply for the emergency, but am running into issues:
1. I need Disconnect/OCP/main bonding jumper ahead of the MTS with GFP
2. We have the neutrals tied at the ATS, therefore we will have two bonding jumpers, one at the Disconnect and one at the MTS.
3. Can I treat them as not separately derived, therefore not needing the bonding jumper at the OCP/disconnect? Note we are industrial so I can take exception to the GFP requirement, though I do have GFP on the MCC.
Any help is appreciated.
We have a 2500A, 3-pole, 4-w, 480v/277v transfer switch (MTS) with main bonding jumper on the normal. The ATS has a 2500AT/2500AF breaker with GFP on the main and swtich only on the emergency source. It feeds an MCC inside a building that has a 2500A main with GFP.
We would like to bring in a second utility to the emergency source (not generator but utility). I use 250.24 for the main service and was thinking to apply for the emergency, but am running into issues:
1. I need Disconnect/OCP/main bonding jumper ahead of the MTS with GFP
2. We have the neutrals tied at the ATS, therefore we will have two bonding jumpers, one at the Disconnect and one at the MTS.
3. Can I treat them as not separately derived, therefore not needing the bonding jumper at the OCP/disconnect? Note we are industrial so I can take exception to the GFP requirement, though I do have GFP on the MCC.
Any help is appreciated.