Seems like his fear was vindicated by Columbia Gas in MA.
Only because it made the news. And things only make the news because they're rare instances.
Seems like his fear was vindicated by Columbia Gas in MA.
Yes it is code compliant.
Yes use separate transfer switches with separate subpanels...
No, there is not any equipment for paralleling small gen-sets...
I was involved with an install with 3-20KW Kohler gensets...6000 gallons of propane buried in the ground.
The owner with the 3 gensets could run 1, 2 or all 3 generators, thereby saving full if they did not need to power all sections of the place.Gen-1 was the more critical circuits such as heat, and refrigerators, etc...
You obviously haven't heard or seen the Honda 2000i portable gensets. They are rated 2000 watts and they are designed to be connected in parallel.
I have two of them in my RV. My AC requires to have both gensets turned on in order to run my 13500 BTU AC unit.
Running just one genset will not even get to start the AC. Not all Honda models can be connected in parallel.
But if OP is going to do this it will be with a couple 20-24 kVA units. I don't know that inverter output units are very common in that large of a unit.You obviously haven't heard or seen the Honda 2000i portable gensets. They are rated 2000 watts and they are designed to be connected in parallel.
I have two of them in my RV. My AC requires to have both gensets turned on in order to run my 13500 BTU AC unit.
Running just one genset will not even get to start the AC. Not all Honda models can be connected in parallel.
I believe that this method is relatively common knowledge. There is no "need" to parallel gensets unless you are trying to provide sufficient power to the single main with generators that are too small.All this discussion about paralleling 20KW generators and there just is not a reason they need to be paralleled.
Post a valid reason to parallel small optional backup generators?
Here is a diagram for the 3-gensets...
The rubber cord ended up at the gensets and not at the sub-panels...
resonable , but one would think not as cost effective as the original 48Kw deal?
Technically speaking, electric heat is more efficient, because all of the energy creates the desired product: heat. Even heat lost in the conductors isn't loss if they're in the living space.Electric heat is extremely inefficient. The efficiency is that much worse with a generator. The BTU heat ratio between gas heat (direct) versus generator electric is about 5:1. A generator will use five units of gas to generate one unit heat. That's because almost 100% of gas translates to heat in the living area. A generator (running on gas) only translates about 20% of the input into electric heat in the living area.
All this discussion about paralleling 20KW generators and there just is not a reason they need to be paralleled. Post a valid reason to parallel small optional backup generators?
Homeowner clearly made an uniformed decision. Your job is to inform them of the problem and/or the costs, and see if they still want to stick with that decision.
Technically speaking, electric heat is more efficient, because all of the energy creates the desired product: heat. ...
...
Exactly.Homeowner clearly made an uniformed decision. Your job is to inform them of the problem and/or the costs, and see if they still want to stick with that decision.
Three subpanels require three separate feeds even if it's one multicore cable. It could be one main interior panel and two subpanels.That's exactly what I will be doing after I gather all the relevant information and options from the brain trust here.
As an aside, clients have no idea how much time I (and I assume you people) spend doing research and planning on their projects. And then they complain if the estimate is not free.
Agree to disagree. You're bringing in data that is not relevant. Electricity production has nothing to do with it, nor does comparing resistance heating to a heat pump."Technically", that's ... just not true. It depends how much waste heat is created in the process of making electricity. It depends if the heating appliance is a heat pump or not. So at best it's an incomplete comparison. It's not even comparing apples to oranges. It's comparing apples to a fruit behind door number 3.
And that's before the economics factors that Golddigger described.
On site generation via an internal combustion engine is what is not efficient. Your losses are in the generator and prime mover. 1000 watt electric heater still has an input of 1000 watts and an output of 1000 watts. What the source of the energy costs can vary greatly also."Technically", that's ... just not true. It depends how much waste heat is created in the process of making electricity. It depends if the heating appliance is a heat pump or not. So at best it's an incomplete comparison. It's not even comparing apples to oranges. It's comparing apples to a fruit behind door number 3.
And that's before the economics factors that Golddigger described.
Now, if we're talking about gas, propane, or gasoline engines, that's different, because engines produce a lot of waste heat in both the exhaust and in the engine-running process.