tying wires?

Status
Not open for further replies.

imBIT!

New member
hey
i need to tie up the conductors of a ct-can with some rope. does anyone have a scamatic to isolate them? if i remember right you tie to the farthest right(or left) then wrap around. and then inbetween. right? wrong? yes? no?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Tori,
Install a peice of fiberglass strut bolted to the back of the the ct can and tie wrap them.
That may not be enough. When a rope tie is specified it is to hold the conductors in place under short circuit current conditions. There are huge magnetic forces developed and tie wraps will not do the job. Look at page 28 of this document.
Don
 

benaround

Senior Member
Location
Arizona
Tori,

I've had it speced. on 1600a 277/480vac, it was for a terminal box to

connect a truck mounted generator set to a 'key type' manual t/s.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Often the installation instructions for panels 800a and larger call for the conductors to be secured with rope.
Don
 
Status
Not open for further replies.
Top