John,
The rule in the 2002 code said:
Don
Yes. The rule is 320 requires a specific ampacity if the cable is in thermal insulation. It leaves no room for the application of the exception in 310.15. This is just like the tap rules in the 2002 code. They were revised in 2005 because the intent of the rule was not being complied with as a result of the same type of reasoning that is being used in this case.Do you feel that 320.80A overrules the exception? I can understand that if it's your interpretation, but I'm not sure I agree with it.
The rule in the 2002 code said:
Many code users looked at this section and then applied the "round-up" rule found in 240.4(B). The code writers never intended that you could use the provisions 240.4(B) for the tap conductor OCPD. The intent was that the ampacity of the conductor be equal or greater than that of the OCPD. In the 2005 code additional wording was added to make the intent of the code rule very clear.(1) Taps Not Over 3 m (10 ft) Long. Where the length of the tap conductors does not exceed 3 m (10 ft) and the tap conductors comply with all of the following:
(1) The ampacity of the tap conductors is
a. Not less than the combined computed loads on the circuits supplied by the tap conductors, and
b. Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent-protective device at the termination of the tap conductors.
I see the logic that was being used to apply 240.4(B) to tap conductor in the same light as the logic being used in this application.(B) Feeder Taps Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The provisions of 240.4(B) shall not be permitted for tap conductors.
Don