grainger said:Can Type Mc cable be used to supply power to a swimming pool. The wire was run inside the house and pvc was run outside. The mc cable was spliced with thwn in an enclosure inside the house.
YES IT DOES BUT THE INSPECTOR SAID IT IS NOT ALLOWEDchris kennedy said:Does the MC have an insulated EGC? 680.25(B)
You don't have to yell at me.:smile:grainger said:YES IT DOES BUT THE INSPECTOR SAID IT IS NOT ALLOWED
curt swartz said:My answer was based on the subject line. If this was a branch circuit feeding a pump and not a feeder I agree with the others that the inspector is incorrect.
Jim W in Tampa said:I would have run it to a small disconect outside then pvc to the pool ,that way its a sub panel.Tell him to give you a number he can back up or sign it off.I think your fine and did more than most.
electricmanscott said:Ok here is your article for YOUR violation and the op's violation...680.25 (A)
The inspector is correct.
mpd said:dennis
the OP says it is a pool feeder
That could mean the swimming pool motor.Can Type Mc cable be used to supply power to a swimming pool. The wire was run inside the house and pvc was run outside. The mc cable was spliced with thwn in an enclosure inside the house.
mpd said:dennis
look at the OP's title