Is there a particular type of conductor that must be used in a Class 1 Division 2 hazardous location? Can I use THHN or XHHW? I'm looking at 2011 NEC Article 501.10 and it's not clear what wiring type I need here. It does not mention THHN or XHHW, so does that mean that that wiring type is prohibited?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
You can use any Table 310.104[2011NEC] conductor as long as it is properly installed within in its own dry/damp/wet and other Art 300 restrictions and is part of a 501.10 (B) wiring method.

I prefer Type XHHW-2.
 