For a Class 1 Division 2, based on article 501.10 (1)(2) liquid tight flexible metal conduit with listed fittings is acceptable?
For a Class 1 Division 2, based on article 501.10 (1)(2) liquid tight flexible metal conduit with listed fittings is acceptable?Liquidtight Flexible Metal Conduit, is not permitted in a Class I, Division 1 location. You must use a "flexible coupling". As I recall a 12" length of 1/2" is over $100. It is also not very flexible, so you will need a longer length than you would use if you could use LFCMC.
View attachment 2582682
Yes, but you originally asked about Class I, Division 1 and that is the question I answered.For a Class 1 Division 2, based on article 501.10 (1)(2) liquid tight flexible metal conduit with listed fittings is acceptable?
You answered my question when the braided type of flex metal conduit was required. Thanks for the help.Yes, but you originally asked about Class I, Division 1 and that is the question I answered.