If the AHJ allows you to install type W cable in a conduit between the bulkhead and the panel location (marina again), can you still use the ampacity table in 400.5(B)?
Dennis Alwon said:Lou-- I don't see why you can't use that table as long as you use the correct column.
The only thing that catches my eye is art. 400.8 (6). Now art. 555.13 does allow conduit to protect cables in certain situations. If you meet these criteria you should be good to go.
Pierre C Belarge said:Lou
Take a look at this site, it would seem that the multiconductor Type W is permitted in ducts (raceways).
http://www.amercable.com/doc/catalogs/industrial/37-432.pdf