Say I have a panel coming from a UL508A panel shop and it is certified as UL 508A compliant. But they're also providing a Type Z purge kit pre-installed.
Do I need to have the purge kit's final installation field certified?
If the AHJ is happy with the purge kit being identified on its own nameplate for Type Z per NFPA 496, and is installed correctly to whatever rigor he may deem necessary (be it visual inspection, asking to confirm the remote alarm, verifying holding pressure), is that equivalent to being suitable/accepted and thus compliant with the law?
Does the AHJ have the right to mandate the installation of the purge kit be field certified by an 3rd party inspection service?
Code references appreciated. I've heard differing opinions on this.
Do I need to have the purge kit's final installation field certified?
If the AHJ is happy with the purge kit being identified on its own nameplate for Type Z per NFPA 496, and is installed correctly to whatever rigor he may deem necessary (be it visual inspection, asking to confirm the remote alarm, verifying holding pressure), is that equivalent to being suitable/accepted and thus compliant with the law?