garnerm
Member
- Location
- Montgomery, AL
:?What should the service entrance ground resistance for a school (any type) measure in ohms? Just a typical. Also, typical, how much would that increase per say ( i know there are alot of varaibles to consider) if you were to go downstream to a branch panel?
My situaltion: School 40+ years old, all original equipment. Replacing the Gym lighting. Feeding a new 277/480V panel from a panel in the same nearby elec. closet for all new lighting circuits. This existing panel has no ground bus. The panel is fed with 3 hots and a netural. The conduit (runs underground) is being used as the grounding electrode conductor. The panel that feeds this one is also the same way, which is fed from the Main Switchboard. This switchboard does have a service entrnce ground from the transformer. The netural and ground were not bonded together, I will be installing a mian bonding jumper at the main and seperating all the grounds from the neturals down stream. Problem: My measure ground resistance at the main switchboard is less than 1 ohm, my measure resistance at the furtherest panel (where my gym is), was measured at over 180 ohms. Is this normal/okay? I think I need to add some additional ground rods due to the age of the conduit feeders. Thoughts are much appreciated.:?
My situaltion: School 40+ years old, all original equipment. Replacing the Gym lighting. Feeding a new 277/480V panel from a panel in the same nearby elec. closet for all new lighting circuits. This existing panel has no ground bus. The panel is fed with 3 hots and a netural. The conduit (runs underground) is being used as the grounding electrode conductor. The panel that feeds this one is also the same way, which is fed from the Main Switchboard. This switchboard does have a service entrnce ground from the transformer. The netural and ground were not bonded together, I will be installing a mian bonding jumper at the main and seperating all the grounds from the neturals down stream. Problem: My measure ground resistance at the main switchboard is less than 1 ohm, my measure resistance at the furtherest panel (where my gym is), was measured at over 180 ohms. Is this normal/okay? I think I need to add some additional ground rods due to the age of the conduit feeders. Thoughts are much appreciated.:?