BigBreakfastJohn
Member
- Location
- South Carolina/USA
- Occupation
- EE
We're a United States' industrial park that owns and operates a 13.8kV delta "grid" that tenant factories can tie into, rather than paying a utility to run a dedicated feed to them. We do not generate, we just have a large amount of capacity from the local utility that we can divide among customer facilities, and we have a long standing agreement with the utility that gives us slightly lower per/kWh and demand charges. Very land-lordish.
A European company is considering joining our site and is asking for us to put pecs in the electrical term sheet for power quality parameters; harmonics, flicker, inrush current, voltage unbalance, fault contribution, grounding method, frequency tolerance, relay coordination, and the standard to be applied. IEEE-519-2022 for harmonics, for example.
Our legal team has asked me what specs we would put in the contract.
I'm new to contracts (and this position, and IEEE), and I believe that they're likely referring to Euronorms EN50160. I understand that most IEEE values for supply voltage tolerance are recommendations, but I've also heard that utilities will put them in contracts anyway, with things like harmonic distortion at the point of common coupling falling under shared responsibility between the POCO and consumer.
I found this table below from an article, I believe these are values that would be expected in a contract for a European grid connection.
My question is:
Is there a United States'/IEEE version of this standards or a list of equivalent standards and specs that I can go off?

A European company is considering joining our site and is asking for us to put pecs in the electrical term sheet for power quality parameters; harmonics, flicker, inrush current, voltage unbalance, fault contribution, grounding method, frequency tolerance, relay coordination, and the standard to be applied. IEEE-519-2022 for harmonics, for example.
Our legal team has asked me what specs we would put in the contract.
I'm new to contracts (and this position, and IEEE), and I believe that they're likely referring to Euronorms EN50160. I understand that most IEEE values for supply voltage tolerance are recommendations, but I've also heard that utilities will put them in contracts anyway, with things like harmonic distortion at the point of common coupling falling under shared responsibility between the POCO and consumer.
I found this table below from an article, I believe these are values that would be expected in a contract for a European grid connection.
My question is:
Is there a United States'/IEEE version of this standards or a list of equivalent standards and specs that I can go off?