My customer has some UF 10-3 to use for a dryer circuit, 70 ft. run. UF rates lower in table 310.60. It says 30 amps, but it is this ok ? Thank you.
yes, sorry, a typo, I had the wrong table number, I meant 310.16 (now 310.15 B 16) And thank you.Yes you can use UF indoors. 310.60 is for Conductors Rated 2001 to 35,000 Volts. The table you need is 310.15(B)(16).
It's a recent purchase, with a ground. Why is is rated lower ? Because of extra thick insulation, heat build up ? Thank youIs it 10/3 with ground? If so not an issue. Years ago they sold 10/3 without a ground and as I don't know how long your customer had the cable I just thought I'd mention it
It's a recent purchase, with a ground. Why is is rated lower ? Because of extra thick insulation, heat build up ? Thank you
It's a recent purchase, with a ground. Why is is rated lower ? Because of extra thick insulation, heat build up ? Thank you
334.80 Ampacity. The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15.
The allowable ampacity shall not exceed that of a 60°C(140°F) rated conductor. The 90°C (194°F) rating shall be
permitted to be used for ampacity adjustment and correction calculations, provided the final derated ampacity does not ex-
ceed that of a 60°C (140°F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall
be determined in accordance with 392.80(A).
What about fire rating ? Is UF insulation fire rated, and ok for indoors ?It has the same temperature rating as NM cable 60° C.
What about fire rating ? Is UF insulation fire rated, and ok for indoors ?
Personally I don't like using UF indoors simply because it's a PITA to strip compared to NM, but that's just me...