UF-B cble for a 480V/1PH pole lighting circuit

Status
Not open for further replies.

jap

Senior Member
Occupation
Electrician
Yes, but it is recommended to space them at least 6 inches from high voltage cables. I don't know how any spacing can be maintained inside a light pole. And there's the 330 foot distance limitation.

Do security and signaling contractors consider 480 high voltage?

JAP>
 

jap

Senior Member
Occupation
Electrician
Ethernet cables are commonly installed in 480 V motor control centers. These are cables with 600 v insulation

I agree.

I consider High Votage 12470 or better.

That's why I don't see why it would be a problem to run a 600v rated security or video cable up the inside of a pole with a sheath on it next to the power conductors.

Is it?


JAP>
 