Part II. Installation
340.10 Uses Permitted. Type UF cable shall be permitted as
follows:
(1) For use underground, including direct burial in the
earth. For underground requirements, see 300.5.
(2) As single-conductor cables. Where installed as singleconductor
cables, all conductors of the feeder grounded
conductor or branch circuit, including the grounded
conductor and equipment grounding conductor, if any,
shall be installed in accordance with 300.3.
(3) For wiring in wet, dry, or corrosive locations under the
recognized wiring methods of this Code.
(4) Installed as nonmetallic-sheathed cable. Where so installed,
the installation and conductor requirements shall
comply with Parts II and III of Article 334 and shall be of
the multiconductor type.
(5) For solar photovoltaic systems in accordance with 690.31.
(6) As single-conductor cables as the nonheating leads for
heating cables as provided in 424.43.