S sparkync Senior Member Location North Carolina Mar 22, 2007 #1 As long as I stay 10 ft. away from the inside wall of the pool, can't I run uf cable to post lamps? Thanks Steve...
As long as I stay 10 ft. away from the inside wall of the pool, can't I run uf cable to post lamps? Thanks Steve...
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 22, 2007 #2 uf uf i vote yes, you can
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 22, 2007 #3 art 680.10 Underground wiring shall not be permitted under the pool or within the area extending 5 feet horizontally from the inside wall of the pool....
art 680.10 Underground wiring shall not be permitted under the pool or within the area extending 5 feet horizontally from the inside wall of the pool....
L lowryder88h Senior Member Location Massachusetts Mar 23, 2007 #4 Uf Uf As said above 680.10 as long as your 5' horizontally away "it be alright"