If a romex connector only lists "NM" and not UF, you can't use it for UF? Is that true? Or is UF covered under "NM" in manufacturer's terms?
What if you get an inspector that doesn't use the whitebook?
A inspector could fail an installation citing 110.3(B) if I used a common NM94 button connector for UF because Arlington only listed NM cable under it's uses?
What if you get an inspector that doesn't use the whitebook?
A inspector could fail an installation citing 110.3(B) if I used a common NM94 button connector for UF because Arlington only listed NM cable under it's uses?
UF can be installed as NM when following 334 part II and III
(4) Installed as nonmetallic-sheathed cable. Where so installed, the installation and conductor requirements shall comply with Parts II and III of Article 334 and shall be of the multiconductor type.