Its been hard to find UF cable 12/4 , basically 2 hots 2 neutrals with ground. Was having a discussion with another guy that was installing his disconnect with receptacle for the hvac unit at a dwelling. He thought he could use regular romex 12/3.. Its a technicality but romex is not rated for outside as his disco will be outside even though the feed is coming from underneath (crawl space) from the house and feeding the back of the disco.
Also the hvac condenser and receptacle shouldn't be sharing neutrals, even from a 'feeder' (NEC definition vs branch circuit) as this would defeat the purpose of of the receptacle if they needed to shut off the breaker for the diso, (shared neutrals must have common disconnect). Is there a code against this on feeder side?
Cant seem to find 12/4 uf as readily and cheap at the big box stores, do they make it often? What do you think of him wanting to share the neutrals on the 'feeder' side? I couldnt find a NEC code that forbade it, just that its not good practice.
Also the hvac condenser and receptacle shouldn't be sharing neutrals, even from a 'feeder' (NEC definition vs branch circuit) as this would defeat the purpose of of the receptacle if they needed to shut off the breaker for the diso, (shared neutrals must have common disconnect). Is there a code against this on feeder side?