Joe.B
- Myrtletown Ca
- Building Inspector
Yes.
Not trying to argue, just genuinely concerned that I'm missing something, here's what I'm looking at:
250.64 (C) Continuous
Except as provided in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections shall be made as permitted in (1) through (4):
(1)Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
(2)Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor.
(3)Bolted, riveted, or welded connections of structural metal frames of buildings or structures.
(4)Threaded, welded, brazed, soldered or bolted-flange connections of metal water piping.
250.68 Grounding Electrode Conductor and Bonding Jumper Connection to Grounding Electrodes
The connection of a grounding electrode conductor at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system and associated bonding jumper(s) shall be made as specified 250.68(A) through (C).
(A) Accessibility
All mechanical elements used to terminate a grounding electrode conductor or bonding jumper to a grounding electrode shall be accessible.
Exception No. 1: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.
Exception No. 2: Exothermic or irreversible compression connections used at terminations, together with the mechanical means used to attach such terminations to fireproofed structural metal whether or not the mechanical means is reversible, shall not be required to be accessible.