I am looking for suggestions on the most effective way to run a Grounding electrode conductor to the footing re bar.
400 amp meter base supplying 2 -200amp load centers.
Our utility will not allow the #4 Cu conductor to enter the meter socket. Is there any reason why the conductor can't be attached to the exterior of the socket with an approved lug?
This would eliminate running individual conductors from each load Center to the rebar.