david
Senior Member
- Location
- Pennsylvania
McGraw-Hill?s
NATIONAL ELECTRICAL CODE 2011 HANDBOOK
K550.10 MOBILE HOMES, MANUFACTURED HOMES, AND MOBILE HOME PARKS page 1313
ARTICLE 550. MOBILE HOMES, MANUFACTURED
HOMES, AND MOBILE HOME PARKS
?550.1. Scope. The provisions of this article cover the electric conductors and equipment installed within or on mobile homes and manufactured homes, and also the conductors that connect mobile homes and manufactured homes to a supply of electricity.
But the service equipment which is located ?adjacent? to the mobile home is covered in Art. 550 and all applicable Code rules on such service equipment?as in Arts. 230 and 250?must be observed.?
No doubt it is a structure but it is also designed to be mobile and article 550 is layout to deal with connecting a potentially mobile structure to a utility.
I think I lean more towards article 550 telling us what mobile home equipment, supply conductors and bonding conductors and provisions of connecting to the service equipment and grounding electrode conductor . 250.32 is called out in 550.32(A) and 250 is called out in 550.32 (B) (4) and (5) and the 550.32 (B) (2) calls out article 230 parts 1 through 7
550.32(B) (5) the manufacturer shall include in its written installation instructions one method of grounding the service equipment at the installation site. The instructions shall clearly state that other methods of grounding are found in Article 250.
Without written installation instructions on connecting a grounding electrode to a manufactured home your not allowed to do it. You?re not going to find that requirement in article 250
NATIONAL ELECTRICAL CODE 2011 HANDBOOK
K550.10 MOBILE HOMES, MANUFACTURED HOMES, AND MOBILE HOME PARKS page 1313
ARTICLE 550. MOBILE HOMES, MANUFACTURED
HOMES, AND MOBILE HOME PARKS
?550.1. Scope. The provisions of this article cover the electric conductors and equipment installed within or on mobile homes and manufactured homes, and also the conductors that connect mobile homes and manufactured homes to a supply of electricity.
But the service equipment which is located ?adjacent? to the mobile home is covered in Art. 550 and all applicable Code rules on such service equipment?as in Arts. 230 and 250?must be observed.?
No doubt it is a structure but it is also designed to be mobile and article 550 is layout to deal with connecting a potentially mobile structure to a utility.
I think I lean more towards article 550 telling us what mobile home equipment, supply conductors and bonding conductors and provisions of connecting to the service equipment and grounding electrode conductor . 250.32 is called out in 550.32(A) and 250 is called out in 550.32 (B) (4) and (5) and the 550.32 (B) (2) calls out article 230 parts 1 through 7
550.32(B) (5) the manufacturer shall include in its written installation instructions one method of grounding the service equipment at the installation site. The instructions shall clearly state that other methods of grounding are found in Article 250.
Without written installation instructions on connecting a grounding electrode to a manufactured home your not allowed to do it. You?re not going to find that requirement in article 250