You are not required by code to install a CEE, you are required to connect to qualifying metal in the footing if it is present though.
If you want a CEE and there isn't qualifying metal present then you can either add qualifying metal or the #4 copper - that is your choice though.
If you have no CEE, no qualifying building steel or qualifying water pipe, then you will need to add an electrode - rod(s) are most common thing used because of relatively low cost and simplicity in such situation.
If you want a CEE and there isn't qualifying metal present then you can either add qualifying metal or the #4 copper - that is your choice though.
If you have no CEE, no qualifying building steel or qualifying water pipe, then you will need to add an electrode - rod(s) are most common thing used because of relatively low cost and simplicity in such situation.