UFER Ground

Status
Not open for further replies.
Don, I agree if the sub panel is connected as a 200 amp bonded equipment per 250.66, otherwise #6 cu still qualifies as a supplementary doesn't it? rbj
 
Last edited:
rbj,
There is no "supplementary" grounding electrode at a second building. 250.32 requires a grounding electrode with the grounding electrode conductor sized per 250.66. The table would require a #4 GEC, and since the grounding electrode being used is a concrete encased electrode, there is no reduction in sized permitted. If it was a ground rod, then 250.66(A) would permit the #6.
Don
 
Don,
Does the 200 A Service main GEC sizing mandate all UFER installations to be #4 even if a 60A sub is installed at a distant structure. I perused through 250.32 earlier and associated the compliance to 250.66 as being relevant to the subpanel supplied using the multi-wire exception. I know there is a wide spread for interpretation here but the 250.32 is pretty well stated
In theory the remote #4 UFER doesn't really hold for transient effects over distance from the main panel, but from a lightning event imposed at the remote structure equipment I can see that rational application. So installing 100 A mains using #6 GEC's on slab footers is the limit....I've installed a few combined garage-agri wells 100A mains way back in the 70's. Now I wonder when 250.32 came into effect? Thanks for the good input. rbj
 
rbj,
Does the 200 A Service main GEC sizing mandate all UFER installations to be #4 even if a 60A sub is installed at a distant structure.
No, the GEC size at the second building is based on the size of the feeder conductors that serve the second building.
I perused through 250.32 earlier and associated the compliance to 250.66 as being relevant to the subpanel supplied using the multi-wire exception.
The exception that you are speaking of does not apply here. It only applies to branch circuits, and in this case we don't have a branch circuit, we have a feeder and the grounding electrode is required by the code rules.
Don
 
The key word 'feeder' is defined with an equivalent final ocpd/disconnect protecting it at the sub panel. I used supplementary incorrectly and I apologize. I have been using the sub ocpd current rating as a base compared to the feeder conductor sizing you have been using as a base per 250.66. We are discussing the same thing from two directions and I think we share a 'gold spike'. The #4 GEC used in a garage UFER connection is good enough to cover all bets for me. Thanks Don. rbj
 