stupid question, but, i've never had to use a concrete encased grounding electrode, so, what do you use to connect the gec to the rebar?....
stupid question, but, i've never had to use a concrete encased grounding electrode, so, what do you use to connect the gec to the rebar?....
I just did a 3 point test on my CEE and compared it to the ground rod at the temp. pole. The ground had 93 ohms while the CEE was 13 ohms.
Why, good exercise. Keeps one young.I hope I never drive another ground rod.
so, i could use a simple ground rod clamp?....ok thanks
so, i could use a simple ground rod clamp?....ok thanks
GROUND CLAMPS LISTED FOR USE ON REBAR
There are currently only (2) “acorn” style clamps listed for use with REBAR:
Erico (Eritech): Model # CP58 - #4 rebar
ILSCO: Models # GRC-38, GRC-48, GRC-68 - #3, 4, and 5 rebar
Other UL listed Clamps for use with REBAR:
Erico (Eritech): Model # EK 16 / EK 17
ILSCO : Model # BGC-2T-DB, BGC-2P-DB, BGC-2PS-DB, BGC-4/0P-DB, BGC-4/0S-DB
Galvan: Model # JRD
Bridgeport: Model # RB-16, RB-17
Regal Fittings: Model # 8181
Consolidated Manufacturing International: Model # JRD
Greaves Corp: Model # J29-DB, J30-DB, J31-DB
NSI Polaris: Model # G140DB / GLC140DB
Sigma Electric: Model # C-11N, C-11BN, C-11, C-11D, C-11DN, RBC-1D
Halex Company: Model # C-11
Thermocraft: Model # JRD, JRD+
Thomas and Betts: Model # CC1C-45R, CC2C- 45R, CC10C-56R, CC20C-56R, CC40C-56R
You have the tester Dennis?
An associate of mine bought a surplus tester 20 years ago for $20.00. It is an old WW II vintage crank style tester. Never used one before but instructions were quite simple. I am sure the accuracy may not be 100% but it appeared to see the difference. I had one rod at about 100 feet away, the next at 60 feet and then about 20 feet to the CEE.
I also tester another job and found with 2 ground rods I only had 88 ohms. I will make sure the contractors don't forget to let me know when they need to pour. The last job the GC forgot to call after I reminded him a few times. I told him the results of my tester and I think he may actually remember next time.
another question, does it matter that the ufer will not be encased in the foundation?....its a huge driveway under a fishing camp...
another question, does it matter that the ufer will not be encased in the foundation?....its a huge driveway under a fishing camp...
Ground rods are being phased out one foundation at a time here in
San Diego. Almost, all new foundations are required to have a CEE
installed for future use. I haven't driven a ground rod(s) in 4 years.
I sure wont miss driving rods that's for sure.
Karl,
What do you mean by "future use"?