ufer ground

Merry Christmas
Status
Not open for further replies.

celtic

Senior Member
Location
NJ
A Ufer clamp

UFER2.GIF



lightning-grounding-clamp-tyco.jpg


PH2974_w.jpg
PH2975_w.jpg
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
stupid question, but, i've never had to use a concrete encased grounding electrode, so, what do you use to connect the gec to the rebar?....


The acorn clamps we use are listed for burial in concrete. I believe most are listed db and for concrete.

I just did a 3 point test on my CEE and compared it to the ground rod at the temp. pole. The ground had 93 ohms while the CEE was 13 ohms. I hope I never drive another ground rod.
 

iwire

Moderator
Staff member
Location
Massachusetts
so, i could use a simple ground rod clamp?....ok thanks

If listed for rebar


GROUND CLAMPS LISTED FOR USE ON REBAR



There are currently only (2) “acorn” style clamps listed for use with REBAR:

Erico (Eritech): Model # CP58 - #4 rebar

ILSCO: Models # GRC-38, GRC-48, GRC-68 - #3, 4, and 5 rebar


Other UL listed Clamps for use with REBAR:

Erico (Eritech): Model # EK 16 / EK 17

ILSCO : Model # BGC-2T-DB, BGC-2P-DB, BGC-2PS-DB, BGC-4/0P-DB, BGC-4/0S-DB

Galvan: Model # JRD

Bridgeport: Model # RB-16, RB-17

Regal Fittings: Model # 8181

Consolidated Manufacturing International: Model # JRD

Greaves Corp: Model # J29-DB, J30-DB, J31-DB

NSI Polaris: Model # G140DB / GLC140DB

Sigma Electric: Model # C-11N, C-11BN, C-11, C-11D, C-11DN, RBC-1D

Halex Company: Model # C-11

Thermocraft: Model # JRD, JRD+

Thomas and Betts: Model # CC1C-45R, CC2C- 45R, CC10C-56R, CC20C-56R, CC40C-56R
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You have the tester Dennis?

An associate of mine bought a surplus tester 20 years ago for $20.00. It is an old WW II vintage crank style tester. Never used one before but instructions were quite simple. I am sure the accuracy may not be 100% but it appeared to see the difference. I had one rod at about 100 feet away, the next at 60 feet and then about 20 feet to the CEE.

I also tester another job and found with 2 ground rods I only had 88 ohms. I will make sure the contractors don't forget to let me know when they need to pour. The last job the GC forgot to call after I reminded him a few times. I told him the results of my tester and I think he may actually remember next time.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
An associate of mine bought a surplus tester 20 years ago for $20.00. It is an old WW II vintage crank style tester. Never used one before but instructions were quite simple. I am sure the accuracy may not be 100% but it appeared to see the difference. I had one rod at about 100 feet away, the next at 60 feet and then about 20 feet to the CEE.

I also tester another job and found with 2 ground rods I only had 88 ohms. I will make sure the contractors don't forget to let me know when they need to pour. The last job the GC forgot to call after I reminded him a few times. I told him the results of my tester and I think he may actually remember next time.

Very interesting Dennis, thank you.

Bob, do you have a link to the thread Bryan post that list on? I tried to save and print that, but it saves as a 'php' file???
 

dezwitinc

Senior Member
Location
Delray Beach, FL
Word of Warning:
Check with your AHJ and find out if you need an inspection before they pour the footer. He may need to see the connection.
It is becoming more commonplace down here that this is a specific inspection.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
another question, does it matter that the ufer will not be encased in the foundation?....its a huge driveway under a fishing camp...


I would think a driveway would qualify but I am not sure as 250.52(A)(3) specifies footer or foundation. I would consider a slab a foundation so..... It would be interesting to know if it would be better than a rod--- I bet it would be.
 

Karl H

Senior Member
Location
San Diego,CA
Ground rods are being phased out one foundation at a time here in
San Diego. Almost, all new foundations are required to have a CEE
installed for future use. I haven't driven a ground rod(s) in 4 years.
I sure wont miss driving rods that's for sure. :D
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Ground rods are being phased out one foundation at a time here in
San Diego. Almost, all new foundations are required to have a CEE
installed for future use. I haven't driven a ground rod(s) in 4 years.
I sure wont miss driving rods that's for sure. :D

Karl,

What do you mean by "future use"?
 