why would you say in this case that rods would be more effective?....it seems that if i used a ufer ground, there would be more surface area in contact with the ground....the reason why i asked about the driveway is b/c in the future lets say they decide to re-do it or take it out, im sure they would destroy the electrode in the process...just thinking out loud here
 

M. D.

Senior Member
why would you say in this case that rods would be more effective?..........


Well I'm thinking that the moisture level will be low , given the shallow depth ,.. Heck I'm not even sure it would be considered a Ufer ,..and depending on the resistivety of the earth rods can have a lower resistance than even a Ufer .. From the link I posted



At a number of sites, separate driven
ground rods were also installed and measured. It was found that in soils of lower
resistivities, i.e., good grounding sites of 5000 Ω-cm or less, rods driven directly
into the soil had lower resistances than encased electrodes. The explanation is that
these soils have resistivities lower than that of typical concrete, hence there is no
advantage to encasement.
 

M. D.

Senior Member
Forget what I said about moisture levels ,.. I see now that you are below moisture level:D
 

NolaTigaBait

Senior Member
Location
New Orleans,LA
well, i'm not really sure what to do here..i can drive 2 rods and be done with it or i can drive the rods and connect to the rebar....it's a fishing camp about 20 feet from the water, so the ground is pretty moist...
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
well, i'm not really sure what to do here..i can drive 2 rods and be done with it or i can drive the rods and connect to the rebar....it's a fishing camp about 20 feet from the water, so the ground is pretty moist...

If you connect to the rebar as a CEE then you dont need to use the ground rods.
 

NolaTigaBait

Senior Member
Location
New Orleans,LA
oh and i forgot.....JEEEEEEEEEEEEZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZUUUUUUUUUUUUUUUUUUUSSSSSSSSSSSSSSSSSSSSSS christ no rebar..........JJJJJJJJJJJJJJJJJJJJEEEEEEEEZZZZZZZZZZZZZZZZZ
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
well, i'm not really sure what to do here..i can drive 2 rods and be done with it or i can drive the rods and connect to the rebar....it's a fishing camp about 20 feet from the water, so the ground is pretty moist...

What is the purpose of this statement if it is inaccurate and there is no driveway. Jeeeeezzzzzz-- you have to drive the ground rods-- what's the problem? You can always add the CEE-- if they remember to call you when they pour the driveway.

You are driving me nuts--:D Of course I don't have far to go.
 

NolaTigaBait

Senior Member
Location
New Orleans,LA
rebar .....5 letters
20 feet of #4 bare ground.....20 letters...
i guess i was being lazy.....should have known it would come back and bite me in the rear on this forum
 

celtic

Senior Member
Location
NJ
Say you pour a slab for a detached building, shed,storage,etc.
Here we have to install a CEE incase a "future" electrical supply
may be needed to supply the detached structure.


The amended version covers that: