Ufer grounding electrode size

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch ufer bonding jumper from #1/0 awg common grounding electrode to ufer of size #4 awg copper correct or is it undersized? Asking because the bonding jumper does extend thru #1/0 awg to other electrodes and grounding electrode conductor bigger than #4 awg.

f2d23a6db12fd0733e3f48ff86f88476.jpg
 
If I am reading the wire sizes correctly, the #4s from the service disconnects with 4'/0 supply are undersized.
Assuming the 1/0 is sized to the service, I see no other problem
 
What size are the service conductors? How did they determine that the #1/0 is the correct size for the GEC?
 
Asking because the bonding jumper does extend thru #1/0 awg to other electrodes and grounding electrode conductor bigger than #4 awg.
What do you mean by this? Your drawing implies that the horizontal line is all #1/0. So the #4 connection to the Ufer ends on the #1/0 common GEC.

Cheers, Wayne
 