Wakeboardr122
Member
- Location
- Lauderdale by the sea, FL,
I understand that the minimum requirement a GEC for ground rods is a #6 because a ground rod cannot displace anymore electric than that of the #6 wire. So it got me thinking, what makes the minimum requirement of a Ufer GEC to be a #4 minimum. I would think it would go off the same theory, the amount of rebar displaced under the building is much more, but less conductive of that of a ground rod? Does anyone know how the code panel came up with this?
To my understanding is in within code compliance to run a #4 ufer, hit my ground rods (2- 6' or more apart) and then tap onto my 1/0 GEC from the water pipe to the first means of disconnect. Unfortunatly around here (Fort Lauderdale, Fl) I just failed inspection using a 1/0 ufer for 400A main service due to the fact the inspectors look at the plans and our engineers do not understand 250.66B (concrete encased electrode not required to be larger than #4) As far as I see it right now its just plain overkill, I'm I looking at this correctly? Thanks
To my understanding is in within code compliance to run a #4 ufer, hit my ground rods (2- 6' or more apart) and then tap onto my 1/0 GEC from the water pipe to the first means of disconnect. Unfortunatly around here (Fort Lauderdale, Fl) I just failed inspection using a 1/0 ufer for 400A main service due to the fact the inspectors look at the plans and our engineers do not understand 250.66B (concrete encased electrode not required to be larger than #4) As far as I see it right now its just plain overkill, I'm I looking at this correctly? Thanks