Most of the users here are working in an area where the NEC is a code requirement. We don't typically get a choice on things. The code says "Do this, don't do that." The code is not a design manual, it is a minimum standard to make electrical systems in the US as safe as they can be.Can you simplify if it is a good ground or not?
To answer the questions you're asking, you probably need an experienced electrical engineer who can get a good analysis of the complete situation, maybe even see it in person. What type of soil is it? What's the ph? How wet is it? There are a bunch of unknow factors.
Also, consider that your application is fairly unique. You have an off-grid system you're trying to design, correct? If the design specifications call for a grounding electrode system, than the designer (you I presume) need to determine what electrodes are available, and if none are, then create one.
It sounds like you've established that you have a CEE. A Concrete Encased Electrode is generally known to be a "good ground", certainly better then a ground rod hammered into the ground.