Pierre, I will be happy to try to answer your questions.
The three sites I have witnessed the damage were located in Ashville, NC. Greenville, NC. and Melbourne, FL. These areas receive quite a bit of precipitation, so I doubt dryness was an issue.
The two NC sites are identical where they are fiber-optic regenerator buildings above ground, and the fiber enters from overhead distribution. The fiber is built into the static wire of a 345 KV transmission line. The fault entered via the fiber metallic sheath. At one site it cracked the concrete, and the other it blew out about 2 cubic feet chunk out of the foundation. The damage occurred where the # 4 AWG entered the foundation.
The Melbourne Fl site is again a fiber optic regenerator, but it is an underground vault referred to as a CEV. This site has the fiber ran under ground. The site was struck on the cover hatch as evident by the burn marks. The hatch cover was bonded to the inside ground halo system. Again the damage was where the # 4 AWG entered the wall of the structure. This damage caused some extra trouble because it broke the water seal, and allowed water to seep in the crack. The sump pumps kept it from becoming a problem, but the fix involved a lot of excavation and a lot of expense.
In all three sites we installed a ground ring, and the problem never has happened again. At the time I was mystified by the damage and asked a few consultants and reps (XIT, RO & Associates, Burndy, and Poly Phaser) if they have ever heard of the problem. They all responded that they have either heard of it or witnessed the problem. The consensus was that the rebar needed to be bonded by either compression connectors or exothermic welds, and the electrode cable needs to be bonded to the rebar in the same fashion. At the time construction was slow and still is, and I had other priorities so I moved on and forgot about it until I seen the thread pop up. So I went back through the construction specifications and found only minimum NEC requirements for the UFER ground. Or in other words no welding or compression connector were used to bond the rebar or GEC cable. Live and learn, next time I will specify if I need to use a UFER again.
TVSS is another subject all together. With respect to installing TVSS on AC services, the ground electrode impedance is not all that important because most AC surges occur on the primary side of the transformer and the surge is in the differential mode and not in the common mode. And if in the common mode the impedance of the GEC makes up the lump of the impedance rather than the electrode impedance itself. For example if the electrode impedance is say 5 ohms, and you have a GEC with a length of say 10 feet. A GEC of # 4 AWG @ length of 10 feet exhibits an impedance of about 2.6 K ohms @ 100 Mhz. 2.6 K ohms in series with 5 ohms is still 2.6 K ohms. Now raise the electrode impedance to 100 ohms in series with 2.6 K ohms and you still have 2.6 K ohms. Will that’s enough about TVSS for now. If you want to know more write me a e-mail or start another post with more specific questions and I will try to answer.
Dereck