Re: Ufer grounds
Roger, any arc be it from lightning, high voltage AC or DC, static, etc contains elements from DC to several hundred megahertz. So it is a mixture. You are correct about there being DC components, but the fast current rise time mimics AC say 10KA in 5 microseconds equates to 200 KHz.
Karl, most surge events are in the differential mode as opposed to common mode. The events occur ahead of the transformer, so when passed through the transformer the potential is from phase-to-neutral, rather than phase-to-ground.
This is why us so called experts advise that your service entrance TVSS only needs protected L-N, the other modes are redundant and only add cost. The common modes like L-G and N-G are already covered by L-N because of the N-G bond requirement on single phase and 4-wire 3-phase services.
Common mode disturbances are generated internally or by a direct strike via lightning hitting the structure. So with this in mind that it why it is advised to use”all-mode” (L-L, L-N, L-G, N-G) devices on sub-panels and end equipment. Keep this in mind, that if it is lightning, the impedance of the EGC's back to the entrance GEC is long and exhibit a high impedance. This is why you see some industries like mine (telecom) use ground grids and bond every sub-panel ground bus directly to the grid in addition to the NEC EGC requirements. This additional bond is much shorter and has much lower high frequency impedance to earth than the EGC circuits.
Hope that helps. Dereck