I have following situation and need some code clarification:
NEC Figure 310.60, Detail 4
The first row - 1st and 2nd Duct contains (3) Single Conductor 750 MCM 15 KV Cable (Third Duct is spare)
The second row - 1st and 2nd Duct contains (3) Single Conductor 750 MCM 15 KV Cable (Third Duct is spare)
The third row - 1st and 2nd Duct contains (3) Single Conductor 500 MCM 15 KV Cable (Third Duct is spare)
In essence I have (3) breakers feeding load via underground duct banks - 1200 A, 1200 A, 800 A.
I am using NEC Table 310.77 one circuit, 90 Degree C, 5001-35,000 Volts ampacities for cable listed above to meet 1200 amp and 800 amp full load requirements. Is this true ? OR do I have to go to six circuit table of Table 310.77 to define the ampacity of each cable used ?
I have 3 breakers feeding load via parallel sets. Is parallel sets in duct bank regarded as separate circuit or single circuit ?. i.e. the first row is really a 1200 amp circuit from a 1200 amp breaker feeding same load.
Your response will be greatly appreciated.