Re: uh oh, another SA question
In 210.52 (B) (1) we are told that ALL countertop outlets covered by 210.52(C),
Notice that I used caps for the word ALL as I quoted the sentence. Also note that the sentence points out that it is the outlets that are required by (C).
What are the outlets required by (C)?
The ones that are to be 2 ft. and 4 ft. apart and any over a 12 inch counter top.
Now that I have fulfilled this requirement I am allowed to go back and install general purpose outlets until my heart is happy.
Pay close attention to the placement of this exception. It is found under the section that is giving the requirement for the counter top receptacles (all countertop outlets covered by 210.52(C)). Another thing to pay close attention to is the wording (as defined) it does not state as required.
The wording of the exception explains that in addition to the required receptacles specified by 210.52, or in other words I can add to these required receptacles or install more if I so desire.
It goes on to tell me that these permitted receptacles are to be supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1.
The exception to 210.70 (A) (1) will let me install a switched receptacle for the required lighting outlet.
The exception under .52 (B) is not talking about the required lighting outlet that is referred to in .70 (A) (1) therefore the words ?as defined?.
Why put this exception under .52 (B) (1) if it was referring to the required lighting outlet? Would not the exception under .70 (A) (1) forbid it?
If this was the case then the exception under .52 (B) (1) would be useless and serve no purpose.
I hope this clears this up.