UL Changes for stacked big breakers?
pago cruiser
Tucson, AZ
Mechanical Designer/Facility Manager
Been awhile since I've been on the forum.
Have a project where we need to replace an existing 4000A Emergency Power Switchboard with an 8000A.
Want to keep the layout the same for spatial and cable tray locations. It does get deeper - no problems.
Provided the requirements to (2) national Panel Board vendors.
Vendor A (who provided the original EP Switchboard) has advised that UL has changed - and no longer allows stacked breakers in a Panel. We currently have (2) Sections, each with a 4000A and a 3000A breaker, stacked. As such, we now need to add an additional (2) sections in order to provide (1) breaker per section.
Vendor B has advised that Vendor A is in error. They have provided a Quote with the 8000A buss, but with stacked breakers.
I know this is not quite germane to NEC , but can anybody shed any light on who is correct on this topic? Yes, there are a myriad of other design issues, and our Engineers are working through those. But the fab of the Switchgear appears to be is UL driven, and it seems difficult to find reference to figure out which vendor is correct.
TIA
There is no UL limitation that I'm aware of (guessing these are 891 switchboards) as long as the equipment is built and tested per UL with their design, it just depends on how the configuration is presented for testing.
Vendor A may not have proposed stack breakers and thus cannot provided it via their listed solution.
They just parallel 1/4"x6" (or 4") bus to get the needed horizontal bus ampacity.
But they would still have to comply with the heat rise and bus bracing requirements of whichever Listing they are trying to get. So simply adding busbars may not be enough.
You said it an emergency power switchboard.
So they are not service entrance rated switchboards?
Just thinking about the newer NEC requirements for multiple service disconnects having to be in separate vertical sections.
I hear UL is revising their standards to match this new NEC requirement. And since many areas are on older codes, it seems like UL may be driving the bus on limiting multiple mains in the same vertical switchboard section.
Maybe that is the issue one manufacturer was talking about.