You might find this useful.,
for example if you have a Challenger apartment cluster meter with original Challenger breakers, you can replace those breakers with Type BR even if the original Challenger label is missing or does not list type BR. The Challenger during the Sylvania era were mostly Type C, and most Eaton BR are dual listed as Type C which has the same result. I've recently confirmed all this with Eaton technical support, based on this letter.
This shows that there are many brands, but only a few actual bus stab types.
Siemens bus stabs are thinner and while the standard BR breakers will insert, the fit is poor.
Eaton sells a line of "classified" breakers which are tested to various panels.
And Connecticut Electric sells a line of "classified" breakers which are simply repackaged Siemens breakers with a label saying they've been tested in certain older panels.
for example if you have a Challenger apartment cluster meter with original Challenger breakers, you can replace those breakers with Type BR even if the original Challenger label is missing or does not list type BR. The Challenger during the Sylvania era were mostly Type C, and most Eaton BR are dual listed as Type C which has the same result. I've recently confirmed all this with Eaton technical support, based on this letter.
This shows that there are many brands, but only a few actual bus stab types.
Siemens bus stabs are thinner and while the standard BR breakers will insert, the fit is poor.
Eaton sells a line of "classified" breakers which are tested to various panels.
And Connecticut Electric sells a line of "classified" breakers which are simply repackaged Siemens breakers with a label saying they've been tested in certain older panels.