Going from memory 334.100?Where does it say what insulation/wire type is used for the conductors in NM cable ?
Going from memory 334.100?
Hey I was close--- Not by the book and too lazy to go upstairs. Or perhaps too old to go upstairs. :smile:Insert old age joke here.
I'll give you a break.:smile:
334.112 insulation.
Hey I was close--- Not by the book and too lazy to go upstairs. Or perhaps too old to go upstairs. :smile:
My memory is very good but it is also very short.:smile:I see my memory is in question also.:smile:
334.112 Insulation.
The insulated power conductors shall be
one of the types listed in Table 310.13 that are suitable for
branch circuit wiring or one that is identified for use in these
cables. Conductor insulation shall be rated at 90?C (194?F).
Ref: (See "ampacity" in NM, in whatever code you happen to be on)NM-B: Nonmetallic-Sheathed Cable. The "B" denotes that individual conductor insulation is rated 90?C; however, ampacity is limited to that for a 60?C conductor (see NEC Section 336-26, 1999 edition). Thermoplastic (PVC) conductor insulation-nylon jacketed, with overall PVC cable jacket.
maybe i didn't ask...the correct question
if the wire was marked, what would it be, thhn , rhw... ? and i know 334. the wire internal to the outer sheath doesn't have any reference to any of the types listed in table 310.16 and i dodn't recall finding it on the packaging of the coil.
334.80what are we using to determine it's rating other than someone at sometime in the beginning of you electrical career said, ok, use the 14-2 for that 15 amp circuit.