UL listing and 110.3B

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Yes, MTW is in the list in Table 310.4 or 310.104 in the older codes.

There is debate on the question of using MTW in a raceway. Like AWM, MTW is intended for internal wiring within equipment.

A quick search says WTTC is Wind Turbine Tray Cable. I have not seen that before. It that is one of the markings, it is tray cable and you can pretty much do anything you want with it, other that exposed single runs.

Really appreciate the great info again!


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Yes, MTW is in the list in Table 310.4 or 310.104 in the older codes.

There is debate on the question of using MTW in a raceway. Like AWM, MTW is intended for internal wiring within equipment.

A quick search says WTTC is Wind Turbine Tray Cable. I have not seen that before. It that is one of the markings, it is tray cable and you can pretty much do anything you want with it, other that exposed single runs.

I just noticed they’re also using TFN wiring for control wiring in conduit.
TFN is not found in 310.4 and is considered fixture wiring. Is this a legit wiring method for this application but poor choice of design?


Sent from my iPhone using Tapatalk
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I just noticed they’re also using TFN wiring for control wiring in conduit.
TFN is not found in 310.4 and is considered fixture wiring. Is this a legit wiring method for this application but poor choice of design?

TFN is legit for Class 1 wiring in dry locations. See post #18 in this thread.
 
Top