Re: UL Listing on Reconditioned Breakers
Interesting...Did you know that a good portion of C-H was the old (W), facilities and personal? Anyway, it's UL that is the key. If it is allowed and listed by UL what does the "old" (W) organization have to do with it?
Also, it is of my personal opinion that the "recondition" breaker may be cleaned and inspected but what determines a pass/fail evaluation? Has the supplier in question been qualified by the OEM to inspect and evaluate the breaker?
NEMA AB4 is generally an accepted method for the guidelines for inspection and prventive maintenance of molded case circuit breakers and does include a field testing. However, an actual calibration check, both thermal and magnetic, to verify that the breaker is within the manufacturers original specifications requires expensive test equipment. When a UL489 breaker is manufactured in a factory UL inspections are commonplace. Fail and inspection/test and the line is shut down.
Relocate that same breaker into the field, either being used or as a stock item, then having it aquired by a reseller or field service organization of some type, how can the NEC be assured that the product meet the requirements as were when originally manufactured?