Ul rating of wire nuts

Status
Not open for further replies.
I used red wire nuts to splice 3 green wires together and to the receptacle.Th AHJ failed this saying that only green wire nuts are acceptable ! Is this true ? I can not find another inspector to agree with the AHJ failer,I also can not find it in the 1999 code which they use.
 

bphgravity

Senior Member
Location
Florida
Re: Ul rating of wire nuts

I do not believe this is a UL issue. There is nothing mechanically different between a red or green wire connector, or any other color wire nut. I also don't believe use is listed on a basis of insulation color. Is it possible that the inspector is citing 250.126(3)? The wording states a GREEN pressure wire connector.... However, I don't feel the code is refering to a "wire nut", but a spring loaded wire terminal on a device. As long as the red wire nut is listed and labeled to handle the three wires you have connected, I do not see this being enforceable.
 

batch

Member
Location
Florida
Re: Ul rating of wire nuts

In all the building codes I have come across it is the AHJ that must provide a specific code referance for the violation. Failure to do so negates the violation notice.
 

luke warmwater

Senior Member
Re: Ul rating of wire nuts

Strukelectric, We work in and around Eastern PA, DE,MD,NJ, and my brother's company works all over Central PA. The consensus is that you've found an inspector that either is making up his own Code, or is mis-interpreting something. He is required to cite the article in which he says you are in violation.
We primarily(90%) use Ideal Tan Twisters. This includes ground tails.
We very rarely use green wirenuts.
Nelco doesn't even make a green wirenut.
Also, check out this link to see what most of these guys are using.
 
Re: Ul rating of wire nuts

I call Ideal and spoke to an engineer,He said only greenies are UL listed for splicing grounds together.They are made with a higher value to handle short circuit loads.News to me.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Ul rating of wire nuts

I call Ideal and spoke to an engineer,He said only greenies are UL listed for splicing grounds together.They are made with a higher value to handle short circuit loads.News to me.
How does the fault current get there if standard wire nuts aren't able to handle short circuit loads? Mike had a newsletter on this about a year ago. He started out with the same info from Ideal that you have, but then the statement was retracted.
Don
 
Re: Ul rating of wire nuts

Originally posted by don_resqcapt19:
I call Ideal and spoke to an engineer,He said only greenies are UL listed for splicing grounds together.They are made with a higher value to handle short circuit loads.News to me.
How does the fault current get there if standard wire nuts aren't able to handle short circuit loads? Mike had a newsletter on this about a year ago. He started out with the same info from Ideal that you have, but then the statement was retracted.
Don
 

luke warmwater

Senior Member
Re: Ul rating of wire nuts

I checked with NELCO, and their statement was their wirenuts are ul/csa approved for grounding(none of which are green). We don't use the brand, but it's an example. Someone sees a Green wirenut and they associate that with grounding, so they assume that all wirenuts used for grounding must be Green.
I don't buy the Ideal statement, and if checked, I would bet that Twisters are also rated for grounding.
I will say that Greenies would be listed Only for grounding.
 

dana1028

Senior Member
Re: Ul rating of wire nuts

This is from the above mentioned Mike Holt newsletter - this is the UL response regarding 'green' wirenuts being required.


Anwer 2: UL Response
Mike ? I?d like to respond to your inquiry to UL regarding the use of twist-on type wire connectors for connecting equipment grounding conductors. I believe that to properly answer this inquiry we need to reference requirements in both the NEC and the guide information which UL provides for listed products.
Sec. 250-8 of the NEC indicates that grounding conductors shall be connected by exothermic welding, listed pressure connectors, listed clamps, or other listed means. Pressure wire connectors are listed under the category of Wire Connectors and Soldering Lugs (UL Guide ZMVV). A ?twist-on? connector is a type of pressure cable connector that is tested to the UL Standard for Splicing Wire Connectors, UL486C. The requirements for these connectors include mechanical securement tests, as well as their ability to carry continuous current within acceptable temperature limits. Listed products in this category are identified by the words ?Wire Connector? (or abbreviation there of) near the UL Listing Mark which may be on the product or smallest unit container. Based on this information, a listed ?Wire Connector,? including the twist-on type, should be suitable for connecting equipment grounding conductors. There was also some question regarding the color of the connector insulation. Listed insulated twist-on type wire connectors are typically provided in a variety of insulation colors, however, to the best of our knowledge we have not listed a wire connector with green color insulation.
NEC Sec. 250-119 requires covered or insulated equipment grounding conductors to have a green or green with yellow stripes outer finish, but there is no NEC requirement for the color of the insulation of a wire connector used to connect equipment grounding conductors.
NEC Sec. 250-8 also permits ?other listed means? for connecting grounding conductors. UL has a category for Grounding and Bonding Equipment (UL Guide KDER). Grounding Connectors are a special type of connector that is tested to the UL467 Standard for Grounding and Bonding Equipment. The requirements for grounding connectors include mechanical securement tests, but unlike wire connectors, these connectors are not subjected to a continuous current test. In lieu of this test, there is a special short time current test in UL467 to show the ability of a grounding connector to safely conduct fault current. There are some listed twist-on type connectors with green color insulation that are listed as grounding connectors. Listed products in this category are identified by the words ?Grounding Connector? (or abbreviation there of) near the UL Listing Mark which may be on the product or smallest unit container.
It should be noted that grounding connectors are only used for connecting grounding conductors, and unlike listed wire connectors, cannot be used to connect current carrying conductors (including grounded and ungrounded conductors). There are some listed Wire Connectors of the twist-on type that are also tested and complementary listed as Grounding Connectors, and the listing mark information for these products will identify them as both. The insulation on these connectors (with both listings) can be various colors, except green. We understand that some jurisdictional authorities may require listed grounding connectors for connecting equipment grounding conductors, and some may require only those with green insulation, and this is certainly permitted by Sec. 90-4 of the NEC. To satisfy this need, the listing categories of ?Grounding Connectors?, and ?Wire Connectors complementary listed as Grounding Connectors? were established for the manufacturers of these products.

I apologize for this somewhat lengthy explanation, but I believe this detailed information is helpful to those who are interested in understanding the rationale behind product requirements and listings of this type. We at UL are always interested in ways to improve our service to the electrical community, and if you or your readers have any suggestions in this regard, please let us know.
Regards, David Dini, P.E. Sr. Research Engineer Underwriters Laboratories Inc. Northbrook, Illinois Phone: 847 664-2982 Fax: 847 509-6285 Email: David.A.Dini@us.ul.com </ym/Compose?To=David.A.Dini@us.ul.com&YY=9037&order=down&sort=date&pos=0>

Mike Holt's Comment: Thank you Dave for taking the time to resolve this issue.
 