I have a scenario in which I have a VFD which is currently being protected by some 60A Class J fuses on the line side. It has been requested of me to add a motor disconnect between the VFD load side and the motor said VFD is controlling. The motor is 25.0HP, 29.50A @ 480 VAC. The motor disconnect that has been specced to use is rated at 30A however it has some conflicting information on the manufacturers website and I'm hoping someone here may be able to clear up this scenario as a whole for me. On the webpage of the device it states that the "SCCR is 65kA RMS Symmetrical when protected with equally sized Class J Fuse", which to me means that if the disconnect is rated at 30A, it would need to be protected by a 30A Class J fuse and all would be well. On the datasheet for the device it reads that its "Suitable for use as a Motor Disconnect per NEC 430-109 (a)(6)Current Rating @ 65,000 RMS Symmetrical Amps up to 600 VAC Max when protected with 40A Class J Fuses, permitting usage at full amperage rating of the switch."
As stated earlier the VFD currently has 60A Class J fuses on its line side, and what I believe we need to do is swap those out for 40A Class J fuses (which will be fine based on the VFD's maximum input current being 33.7A) to adhere to the datasheets specs on the motor disconnect. Is this the correct train of thought? I assume that if we were to keep the 60A Class J fuses protecting the VFD, add the motor disconnect on the load side of the VFD, then the SCCR for that branch and subsequently the entire enclosure would be reduced to only 5kA. Is another option here to keep the 60A Class J fuses on the line side of the VFD but then place another set of 40A Class J fuses on the load side of the VFD prior to the motor disconnect? Which seems not correct to me but was suggested by a colleague and I would like to make sure that I am not the only one whom thinks that's "not ok". Yet another option suggested was to just get a higher amperage rated disconnect whos specs stated that it needed to be protected by 60A Class J fuses, which from this manufacturer would mean a 40A disconnect.
In addition to the above, another VFD within the enclosure is protected by 25A Class CC fuses and is required to have a motor disconnect as well. The issue with this branch is that the 20/25A disconnect from the same manufacturer also requires it to be protected by 40A Class J fuses in order to achieve its 65kA SCCR rating. This problem with this branch is that the maximum allowable fuse size to meet the UL 61800-5-1 requirements of the VFD manufacturer have the fuse size capped at 30A, which is less than the aforementioned 40A requirement of the motor disconnect, so what do I do with this branch to achieve the 65kA SCCR?
As stated earlier the VFD currently has 60A Class J fuses on its line side, and what I believe we need to do is swap those out for 40A Class J fuses (which will be fine based on the VFD's maximum input current being 33.7A) to adhere to the datasheets specs on the motor disconnect. Is this the correct train of thought? I assume that if we were to keep the 60A Class J fuses protecting the VFD, add the motor disconnect on the load side of the VFD, then the SCCR for that branch and subsequently the entire enclosure would be reduced to only 5kA. Is another option here to keep the 60A Class J fuses on the line side of the VFD but then place another set of 40A Class J fuses on the load side of the VFD prior to the motor disconnect? Which seems not correct to me but was suggested by a colleague and I would like to make sure that I am not the only one whom thinks that's "not ok". Yet another option suggested was to just get a higher amperage rated disconnect whos specs stated that it needed to be protected by 60A Class J fuses, which from this manufacturer would mean a 40A disconnect.
In addition to the above, another VFD within the enclosure is protected by 25A Class CC fuses and is required to have a motor disconnect as well. The issue with this branch is that the 20/25A disconnect from the same manufacturer also requires it to be protected by 40A Class J fuses in order to achieve its 65kA SCCR rating. This problem with this branch is that the maximum allowable fuse size to meet the UL 61800-5-1 requirements of the VFD manufacturer have the fuse size capped at 30A, which is less than the aforementioned 40A requirement of the motor disconnect, so what do I do with this branch to achieve the 65kA SCCR?