doomed9
Member
- Location
- Hopkinton, MA
- Occupation
- Control Systems Designer
I am designing a UL508a panel that has a MCCB of 125A acting as my disconnect switch. Downstream of that disconnect I am looking to install a UL listed power distribution block to connect to my branch circuits. The PDB accepts 1 AWG wire Line side, however load side it only accepts a 4-14 AWG. I want to connect 8 AWG wire to it as I need 50A for my branch circuits. Am I allowed to connect lower ampacity wires to the load side of a PDB if I used circuit protection soon after the PDB? Thank you for any help.