I have been having a discussion with several fellow engineers here about the use of electrical interlocks versus mechanical interlocks for UL508a ICP disconnecting means. This came up because a project may end up needing a 2500A main CB and they do not have the common mechanical means by which to interlock them with the enclosure doors, so the use of a spring loaded solenoid lock with a key operated switch to release the solenoid.
Here is the relevant UL508a section.
It appears to me that a key operated solenoid locking mechanism (spring loaded to unlock) clearly fails 66.1.5.1 on both clause a and b. This is my logic.
Read the requirements carefully, and then consider what would happen if the control circuit to the lock were to fail (say the fuse blows).
The main CB would still be closed but the interlock would be defeated, thus violating the requirement in clause (a) that a tool be required to defeat the interlock.
The same problem exists with clause (b). If the control circuit is de-energized (say that someone was working on the circuit and forgot to turn it back on), the interlock will not re-engage when the door closes.
Here is the relevant UL508a section.
66.1.5 A door of an enclosure that gives access to uninsulated live parts operating at 50 volts rms ac or
60V dc or more shall be interlocked with the disconnecting means such that none of the doors can be
opened unless the power is disconnected.
Exception: A disconnecting means for maintenance lighting circuits or for power supply circuits to control
devices with memory requiring power at all times are not required to be interlocked with the enclosure
doors. The cautionary marking in 55.4 shall be provided.
Revised 66.1.5 effective March 1, 2007
66.1.5.1 The interlocking means required by 66.1.5 shall be provided with all the following:
a) Means to defeat the interlock without removing power and which requires the use of a tool to
operate;
b) Means to prevent restoring power while the enclosure doors are open unless a defeat
mechanism is operated; and
c) Reactivated automatically when all the doors are closed.
It appears to me that a key operated solenoid locking mechanism (spring loaded to unlock) clearly fails 66.1.5.1 on both clause a and b. This is my logic.
Read the requirements carefully, and then consider what would happen if the control circuit to the lock were to fail (say the fuse blows).
The main CB would still be closed but the interlock would be defeated, thus violating the requirement in clause (a) that a tool be required to defeat the interlock.
The same problem exists with clause (b). If the control circuit is de-energized (say that someone was working on the circuit and forgot to turn it back on), the interlock will not re-engage when the door closes.